Re: BS Vignette- Second Attempt

Postby Sparky83 » Fri Jan 12, 2018 11:10 am

Dampers should be placed in the center of the wall thickness.
No flex visible at the SE corner of the conference room.
Need to see sketch circles to evaluate accent lights. Most likely too close to each other and too far from the north and south walls.
No air movement in the center of the conference room.
Sparky83
 
Posts: 7649
Joined: Tue Dec 02, 2014 1:36 pm

Re: BS Vignette- Second Attempt

Postby krissmZ » Sun Jan 14, 2018 11:47 am

The drafting room should be more evenly distributed with the diffusers and returns. Alternate so they aren't all crowded on one side of the room.
In the file room diffuser and returns should be a min of 4' apart.
Diffusers too close to the wall in the reception, drafting and conference rooms. I believe the rule is 1' min for diffusers and 6" min for returns, but don't take my word on that. The best practice is to try to centralize while, evenly distributing throughout the space.
krissmZ
 
Posts: 66
Joined: Sun Apr 26, 2015 5:01 pm

Re: BS Vignette- Second Attempt

Postby Sparky83 » Mon Jan 15, 2018 5:11 am

krissmZ wrote:The drafting room should be more evenly distributed with the diffusers and returns. Alternate so they aren't all crowded on one side of the room. Works just fine as is.
In the file room diffuser and returns should be a min of 4' apart.
Diffusers too close to the wall in the reception, drafting and conference rooms. I believe the rule is 1' min for diffusers and 6" min for returns, but don't take my word on that. Not always possible.The best practice is to try to centralize while, evenly distributing throughout the space.
Sparky83
 
Posts: 7649
Joined: Tue Dec 02, 2014 1:36 pm