Mechanical & Electrical Plan Vignette and Multiple Choice

BS Vignette second try

Postby jianglimeng1231 » Wed Sep 13, 2017 9:12 pm

Please see my attached and provide any advice you have in mind!
Your opinion values a lot to me!
Thank you:)
You do not have the required permissions to view the files attached to this post.
jianglimeng1231
 
Posts: 17
Joined: Sat Mar 26, 2016 11:42 am

Re: BS Vignette second try

Postby Sparky83 » Thu Sep 14, 2017 4:05 am

Poor separation between supply & return in the file room and reception. Min 4' is recommended.
Uneven HVAC layout in the studio. Think symmetry.
Accent light and return grille occupy the same space in the architect's office.
Sparky83
 
Posts: 7649
Joined: Tue Dec 02, 2014 1:36 pm

Re: BS Vignette second try

Postby jianglimeng1231 » Thu Sep 14, 2017 6:29 pm

Thanks!!! Your opinion is so valuable to me!