Vingette for review please

Mechanical & Electrical Plan Vignette and Multiple Choice

Vingette for review please

Postby dollydavis33 » Tue Oct 09, 2012 9:26 pm

I think my solution is pretty close to the NCARB passing solution (not that that means I did it right), but I did a few things differently. I just looked over my solution and think my conference room lighting might be incorrect, I overlit, which I think is okay, but noticed that I didn't center the lights in the space. Any other comments are greatly appreciated...thanks!
You do not have the required permissions to view the files attached to this post.
dollydavis33
 
Posts: 6
Joined: Tue Oct 09, 2012 9:19 pm

Re: Vingette for review please

Postby Coach » Tue Oct 09, 2012 11:08 pm

2x4 spacing is incorrect.
Supply and return grilles should be separated by 4' min.
Take ducts a snap or two into risers.
Bring supply out of riser to east, move both branches west, and save about 20' of duct.
Supply closet light spacing incorrect.
User avatar
Coach
Site Admin
 
Posts: 13249
Joined: Wed May 23, 2012 2:08 am

Re: Vingette for review please

Postby Bman77 » Wed Oct 10, 2012 4:57 am

I know this has probably been posted elsewhere but I feel the need to ask anyways, the lighting diagrams for the 2x2 only extends to 2ft beyond the light for the required FC, in this solution it seems that the 2x2 go are attempting to go beyond this threshold. Does anyone have an explanation of when such liberties should be taken?
Bman77
 
Posts: 2
Joined: Wed Oct 10, 2012 4:21 am

Re: Vingette for review please

Postby Coach » Wed Oct 10, 2012 1:51 pm

Bman77 wrote:I know this has probably been posted elsewhere but I feel the need to ask anyways, the lighting diagrams for the 2x2 only extends to 2ft beyond the light for the required FC, in this solution it seems that the 2x2 go are attempting to go beyond this threshold. Does anyone have an explanation of when such liberties should be taken?

Distance between fixtures should be 2x diagram distance. Max distance to wall is diagram + 12".
User avatar
Coach
Site Admin
 
Posts: 13249
Joined: Wed May 23, 2012 2:08 am

Re: Vingette for review please

Postby dollydavis33 » Wed Oct 10, 2012 2:07 pm

Understood.

Thank you Coach!
dollydavis33
 
Posts: 6
Joined: Tue Oct 09, 2012 9:19 pm

Re: Vingette for review please

Postby Bman77 » Thu Oct 11, 2012 4:59 am

Ok, I will look for this tonight but maybe you can you explain where you found the max distance to the wall is diagram +12"?

Thanks!!
Bman77
 
Posts: 2
Joined: Wed Oct 10, 2012 4:21 am

Re: Vingette for review please

Postby Coach » Thu Oct 11, 2012 2:30 pm

Bman77 wrote:Ok, I will look for this tonight but maybe you can you explain where you found the max distance to the wall is diagram +12"?

Just common knowlwedge. Light bounces off wall.
User avatar
Coach
Site Admin
 
Posts: 13249
Joined: Wed May 23, 2012 2:08 am

Re: Vingette for review please

Postby eyoung » Sun Mar 03, 2013 12:17 pm

Supply diffuser is missing flex duct connecting it to rigid in Supply Closet. If youre pushing the 10ft limit for flex duct in the Drafting Studio, you could run it to the south branch along the bearing wall.
eyoung
 
Posts: 27
Joined: Sat Mar 02, 2013 2:11 pm