Vignette - First Attempt

Mechanical & Electrical Plan Vignette and Multiple Choice

Vignette - First Attempt

Postby pcare » Sat Jun 16, 2018 7:21 am

Please review - would greatly appreciate any comments. Thanks!
BS_sm.jpg
You do not have the required permissions to view the files attached to this post.
pcare
 
Posts: 21
Joined: Sun Mar 16, 2014 9:36 am

Re: Vignette - First Attempt

Postby pcare » Sun Jun 17, 2018 5:55 am

Just noticed that the grid in the conference room is misaligned - please ignore that error.
pcare
 
Posts: 21
Joined: Sun Mar 16, 2014 9:36 am

Re: Vignette - First Attempt

Postby Sparky83 » Thu Jun 28, 2018 8:44 am

Incorrect spacing for all 2x4 lights.
Inadequate accent lighting.
Dampers should be centered in the wall thickness.
Return duct is too long.
Poor separation between supply & return in the supply closet, file room and architect's office. Min 4' separation is recommended.
Inadequate HVAC in reception.
Inefficient rigid duct layout.
Sorry, very clearly failing.