1st Attempt BS RCP Vignette

Mechanical & Electrical Plan Vignette and Multiple Choice

1st Attempt BS RCP Vignette

Postby jacopast » Sun Apr 22, 2018 3:42 pm

Thank you in advance. Any comments welcome.

Capture.JPG
You do not have the required permissions to view the files attached to this post.
jacopast
 
Posts: 5
Joined: Mon Sep 14, 2015 11:09 am

Re: 1st Attempt BS RCP Vignette

Postby Sparky83 » Mon Apr 23, 2018 4:46 am

Supply closet is severely over lit.
Rigid fails to connect over reception. MAJOR error.
Rotate 2x4 lights in the architect's office for more uniform coverage.
Too many accent lights and too close to the wall.
Rigid duct layout does not allow for flexibility in locating diffusers. There is a large area that cannot be reached with a max 10' flex.
Sparky83
 
Posts: 7649
Joined: Tue Dec 02, 2014 1:36 pm