Mechanical & Electrical Plan Vignette and Multiple Choice
by mandyk650 » Wed Apr 18, 2018 9:45 pm
Please review! I am still very nervous about this vignette.
Thanks!
Amanda
You do not have the required permissions to view the files attached to this post.
-
mandyk650
-
- Posts: 50
- Joined: Wed Sep 23, 2015 7:21 pm
by wws341234 » Wed Apr 18, 2018 10:56 pm
Check the radius for the accent lighting in AO, seems a bit big and under lit. The diffuser and return grill looks a bit too close to each other near the accent lighting. lighting in CR are positioned too close to each other.
-
wws341234
-
- Posts: 112
- Joined: Wed Apr 02, 2014 6:49 am
by Coach » Thu Apr 19, 2018 12:03 am
Incorrect light spacing in AO, conf, and file.
Accents underlit.
Maintain 4' min separation between supply and return grilles.
Work on more uniform are distribution and keeping supplies away from walls.
If you move middle rigid run to west you can exit shaft to east and eliminate rigid south of shaft.
Drafting lighting not centered.
Returns must be oriented parallel to short side of tile.
-
Coach
- Site Admin
-
- Posts: 13249
- Joined: Wed May 23, 2012 2:08 am