Vignette review

Mechanical & Electrical Plan Vignette and Multiple Choice

Vignette review

Postby hepsy » Thu Apr 05, 2018 11:16 am

lighting vignette-arecoach.jpg
Please provide comments on my vignette. I am also curious about supply closet and the lighting in there. I choose two 2x2 lights but exam guide shows one 2x4 which under lights space.
You do not have the required permissions to view the files attached to this post.
hepsy
 
Posts: 50
Joined: Sun Jul 06, 2014 9:26 pm

Re: Vignette review

Postby Sparky83 » Fri Apr 06, 2018 9:17 am

Incorrect 2x4 light spacing in the architect's office.
Return grilles in the studio will fall out. See NE and NW corners. They are not properly supported by the grid.
Extend flex to the center of diffusers, not the edge.
Wasted rigid duct in the file room.
Place dampers in the middle of the wall thickness.
Sparky83
 
Posts: 7649
Joined: Tue Dec 02, 2014 1:36 pm