Vignette - Please Comment!

Mechanical & Electrical Plan Vignette and Multiple Choice

Vignette - Please Comment!

Postby onlytheclouds » Sun Mar 25, 2018 9:00 am

Please comment with corrections/recommendations!
You do not have the required permissions to view the files attached to this post.
onlytheclouds
 
Posts: 45
Joined: Sat Dec 06, 2014 1:19 pm

Re: Vignette - Please Comment!

Postby Sparky83 » Mon Mar 26, 2018 4:43 am

NEVER mix 2x2 and 2x4 lights in a room. It is impossible to space them correctly when doing so.
No air circulation on the west side of the architect's office.
Incorrect 2x4 light spacing in the architect's office and conference roomm.
Do not bend the rigid duct inside the riser shaft. Difficult to construct and accomplishes nothing.
Accent lights cannot overlap the grid.
Poor separation between supply & return in the conference room. Min 4' is recommended.
Sparky83
 
Posts: 7649
Joined: Tue Dec 02, 2014 1:36 pm

Re: Vignette - Please Comment!

Postby onlytheclouds » Mon Mar 26, 2018 7:49 am

Sparky83, THANK YOU!
onlytheclouds
 
Posts: 45
Joined: Sat Dec 06, 2014 1:19 pm