Vignette 1st Attempt - Corrections and Advice Appreciated!

Mechanical & Electrical Plan Vignette and Multiple Choice

Vignette 1st Attempt - Corrections and Advice Appreciated!

Postby onlytheclouds » Wed Mar 14, 2018 6:35 pm

Corrections and/or advice appreciated. Thank you in advance!
You do not have the required permissions to view the files attached to this post.
onlytheclouds
 
Posts: 45
Joined: Sat Dec 06, 2014 1:19 pm

Re: Vignette 1st Attempt - Corrections and Advice Appreciate

Postby Sparky83 » Thu Mar 29, 2018 7:13 am

Incorrect spacing for all 2x4 lights.
Accent lights are too far from the wall.
Do not bend the rigid duct inside the riser shaft. Difficult to construct and accomplishes nothing. Ducts may be placed above lights.
Poor separation between supply & return in the architect's office, conference room and studio. Min 4' is recommended.
Sorry, this would not pass.
Sparky83
 
Posts: 7649
Joined: Tue Dec 02, 2014 1:36 pm


Return to BS - BUILDING SYSTEMS