Just tried this one, tougher than I thought.....
Not sure about the requirements for the accent lights, should those circles just "touch the wall" or should they cut into the wall without any area being a little underlighted?
You do not have the required permissions to view the files attached to this post.
Archer40
 
Posts: 145
Joined: Thu Jul 14, 2016 8:51 pm

Re: Ncarb First Try

Postby Sparky83 » Tue Feb 06, 2018 4:21 pm

Incorrect spacing for all 2x4 lights.
Rigid duct should NOT branch or bend inside the riser shaft. As shown is not buildable and is missing a damper.
Connect flex to the center of diffusers, not the edge.
Need to see sketch circles to evaluate accent lights.
2 return grilles in the studio will fall out.
No air movement on the west end of the architect's office.
Sparky83
 
Posts: 7649
Joined: Tue Dec 02, 2014 1:36 pm

Re: Ncarb First Try

Postby Archer40 » Tue Feb 06, 2018 9:41 pm

Sparky83 wrote:Incorrect spacing for all 2x4 lights.
Rigid duct should NOT branch or bend inside the riser shaft. As shown is not buildable and is missing a damper.
Connect flex to the center of diffusers, not the edge.
Need to see sketch circles to evaluate accent lights.
2 return grilles in the studio will fall out.
No air movement on the west end of the architect's office.


Thank you Sparky83! Very helpful comments!