NCARB Vignette_please review!

Mechanical & Electrical Plan Vignette and Multiple Choice

NCARB Vignette_please review!

Postby kek123 » Tue Jan 02, 2018 2:37 pm

Second attempt at vignette. Comments?

IMG_0058.JPG
You do not have the required permissions to view the files attached to this post.
kek123
 
Posts: 39
Joined: Sat Oct 03, 2015 10:18 am

Re: NCARB Vignette_please review!

Postby Sparky83 » Tue Jan 02, 2018 7:02 pm

The diffuser in the file room will fall out.
Incorrect 2x4 light spacing.
Uneven HVAC layout in the studio.
Dampers should be centered in the wall thickness.
Sparky83
 
Posts: 7649
Joined: Tue Dec 02, 2014 1:36 pm

Re: NCARB Vignette_please review!

Postby kek123 » Wed Jan 03, 2018 8:28 am

Thanks Sparky - I cannot figure out a layout in the architects office that would be appropriate lighting. Do you have a solution? What am I missing?

For the supply and return - what would you say is the rule of thumb for evenly spacing them?

Can't believe I missed the return being oriented incorrectly! Thanks for pointing that out!
kek123
 
Posts: 39
Joined: Sat Oct 03, 2015 10:18 am

Re: NCARB Vignette_please review!

Postby Sparky83 » Wed Jan 03, 2018 10:11 am

kek123 wrote:Thanks Sparky - I cannot figure out a layout in the architects office that would be appropriate lighting. Do you have a solution? What am I missing? Use both lighting charts for 2x4 lights and always space accordingly.

For the supply and return - what would you say is the rule of thumb for evenly spacing them? Symmetry.

Can't believe I missed the return being oriented incorrectly! Thanks for pointing that out!
Sparky83
 
Posts: 7649
Joined: Tue Dec 02, 2014 1:36 pm


Return to BS - BUILDING SYSTEMS