Postby kek123 » Sat Dec 30, 2017 10:05 am

First attempt at Ncarb provided BS vignette - With the room dimensions you can't get a perfect 50 fc everywhere so I was wondering is it better to lean on the side of overlighting or underlighting? Or am I missing something completely here? Any reason this would fail?
You do not have the required permissions to view the files attached to this post.
kek123
 
Posts: 39
Joined: Sat Oct 03, 2015 10:18 am

Re: PLEASE REVIEW_Building Systems Vignette

Postby Sparky83 » Sat Dec 30, 2017 2:47 pm

Lighting will never be perfect. Just get as close as you can.
Architect's office is severely under lit. It is very unlikely that you can solve any vignette with only 1 type of light.
Poor separation between supply & return in the supply closet and studio. Min 4' is recommended.
Dampers should be centered in the wall thickness.
Wasted rigid duct on the north side of the architect's office.
Why are there 2 rigid ducts above the file room?
Need see to circles to evaluate accent lights.
Sparky83
 
Posts: 7649
Joined: Tue Dec 02, 2014 1:36 pm

Re: PLEASE REVIEW_Building Systems Vignette

Postby kek123 » Tue Jan 02, 2018 2:29 pm

Very helpful thank you!