Vignette Attempt - Testing Tomorrow!

Mechanical & Electrical Plan Vignette and Multiple Choice

Vignette Attempt - Testing Tomorrow!

Postby jemaier » Thu Dec 21, 2017 4:05 am

Any feedback would be greatly appreciated!

A couple of questions:
I'm wondering if my fire damper position is correct?
Is it okay to have flexible ducts connecting to the rigid ducts directly across from eachother - would they be considered separate ducts or would their lengths be combined?
It's not in the program, but should there be a minimum distance between the ducts (rigid or flexible) and any ceiling fixtures?

Thanks!
You do not have the required permissions to view the files attached to this post.
jemaier
 
Posts: 4
Joined: Fri Feb 05, 2016 4:08 pm

Re: Vignette Attempt - Testing Tomorrow!

Postby Coach » Thu Dec 21, 2017 4:32 pm

jemaier wrote:I'm wondering if my fire damper position is correct?

Long leg should be in middle of wall.

Is it okay to have flexible ducts connecting to the rigid ducts directly across from each other

Yes, but extend rigid past that point.

- would they be considered separate ducts or would their lengths be combined?

They're separate but you have to draw them independently.

It's not in the program, but should there be a minimum distance between the ducts (rigid or flexible) and any ceiling fixtures?

No, they're at different planes.

Return grilles must be parallel to short side of tile.