Postby tallow » Sat Nov 25, 2017 2:31 pm

First attempt at BS vignette. Had a tough time coming up with a decent lighting layout for the Arch. Office. Any comments much appreciated.
You do not have the required permissions to view the files attached to this post.
tallow
 
Posts: 27
Joined: Sat Feb 01, 2014 12:03 pm

Re: BS Vignette - Take One

Postby Sparky83 » Sat Nov 25, 2017 2:43 pm

Return grilles in reception and supply closet will fall out. They should be properly supported by the grid.
Poor separation between supply & return in the supply closet and conference room. Min 4' is recommended.
Rotate 2x4 lights in the architect's office for more uniform coverage.
Inadequate accent lighting. Too far apart and too far from the wall.
Illegal rigid duct location. East/west is not within 2' of a bearing wall or beam. Fatal.
DO NOT bend the rigid duct inside the riser shaft. That is difficult to construct and accomplishes nothing.
Sparky83
 
Posts: 7649
Joined: Tue Dec 02, 2014 1:36 pm

Re: BS Vignette - Take One

Postby tallow » Sat Nov 25, 2017 2:58 pm

Thanks a million Sparky, will keep all that in mind. Made a poor assumption there on the extent of the bearing wall.
tallow
 
Posts: 27
Joined: Sat Feb 01, 2014 12:03 pm