BS Vignette - Comments Appreciated!

Mechanical & Electrical Plan Vignette and Multiple Choice

BS Vignette - Comments Appreciated!

Postby Nick » Tue Nov 14, 2017 8:12 pm

Comments appreciated. Thanks!
You do not have the required permissions to view the files attached to this post.
Nick
 
Posts: 9
Joined: Sat Jun 28, 2014 11:25 am

Re: BS Vignette - Comments Appreciated!

Postby Sparky83 » Wed Nov 15, 2017 5:36 am

Grilles in reception and file room will fall out. They are not supported properly by the grid.
Rigid layout does not provide for flexibility in diffuser locations per the program. With a max 10' flex, a large area cannot be reached.
Rigid ducts ban branch. Adding an extra damper wastes $$$.
Sparky83
 
Posts: 7649
Joined: Tue Dec 02, 2014 1:36 pm

Re: BS Vignette - Comments Appreciated!

Postby Nick » Wed Nov 15, 2017 9:56 pm

Thanks for the assist. Can you explain the following comments?

With a max 10' flex, a large area cannot be reached. (all flex is under 10' in the plan)

Rigid ducts ban branch. (?)

Thanks again.
Nick
 
Posts: 9
Joined: Sat Jun 28, 2014 11:25 am

Re: BS Vignette - Comments Appreciated!

Postby Sparky83 » Thu Nov 16, 2017 5:59 am

Nick wrote:Thanks for the assist. Can you explain the following comments?

With a max 10' flex, a large area cannot be reached. (all flex is under 10' in the plan)

Rigid ducts ban branch. (?)

Thanks again.

From the program:

The client wants flexibility for furniture placement, effcient lighting levels, and a comfortable environment.



Rigid layout does not provide for flexibility in diffuser locations per the program.
Sparky83
 
Posts: 7649
Joined: Tue Dec 02, 2014 1:36 pm