Postby Michelle » Sat Nov 04, 2017 9:50 pm

Hi this is my first try of the BS vignette. Please leave you comments.
Big question: is it underlighting?

Thank you in advance for your help.
You do not have the required permissions to view the files attached to this post.
Michelle
 
Posts: 78
Joined: Wed Sep 02, 2015 6:27 am

Re: Vignette Help

Postby Sparky83 » Sun Nov 05, 2017 6:22 am

Architect's office and conference room are severely under lit.
Inadequate accent lighting, and they overlap the grid.
Grilles in the conference room, supply closet, file room and architect's office will fall out.
DO NOT bend the rigid duct inside the riser shaft. This is hard to build and accomplishes nothing.
Supply duct could be considered to not connect to the riser.
The rigid duct layout does not provide for flexibility in the placement of diffusers as required in the program. There are large areas that cannot be reached with a max 10' flex.
Sparky83
 
Posts: 7649
Joined: Tue Dec 02, 2014 1:36 pm