Vignette 4.0 - 2nd Attempt

Mechanical & Electrical Plan Vignette and Multiple Choice

Vignette 4.0 - 2nd Attempt

Postby fare75 » Sat Nov 04, 2017 8:07 am

1212.jpg

3 days to go!
any tips on determine using 2x4 or 2x2 fluorescent fixtures & grid orientation? This part took me quite a long time trial & error...

grills above the door...does it matter?
You do not have the required permissions to view the files attached to this post.
fare75
 
Posts: 195
Joined: Sun Mar 22, 2015 10:35 am

Re: Vignette 4.0 - 2nd Attempt

Postby Sparky83 » Sun Nov 05, 2017 6:19 am

Grilles not supported properly by the grid will fall out. See studio and reception.
Poor separation between supply & return in the file room and studio. Min 4' is recommended.
Max flex length exceeded in reception.
Accent lights are too far from the wall. Sketch circles should intersect each other at the face of the wall.
Sparky83
 
Posts: 7649
Joined: Tue Dec 02, 2014 1:36 pm

Re: Vignette 4.0 - 2nd Attempt

Postby fare75 » Sun Nov 05, 2017 7:23 am

Sparky83 wrote:Grilles not supported properly by the grid will fall out. See studio and reception.
Poor separation between supply & return in the file room and studio. Min 4' is recommended.
Max flex length exceeded in reception.
Accent lights are too far from the wall. Sketch circles should intersect each other at the face of the wall.

Very useful comment! Will try again later today!
fare75
 
Posts: 195
Joined: Sun Mar 22, 2015 10:35 am