BS - Vignette Attempt - Please Review!

Mechanical & Electrical Plan Vignette and Multiple Choice

BS - Vignette Attempt - Please Review!

Postby bradfordpayne » Wed Oct 18, 2017 9:34 am

Retry at this. I calculated the 2x4 lights to be 4' spacing on the 2' end and 6' spacing on the 4' end. I still have the accent lights at 4' spacing, but overlapped the sketch circles to give more of a 1'-8" spacing. Is this correct?
Is there adequate air movement in the studio now?
You do not have the required permissions to view the files attached to this post.
bradfordpayne
 
Posts: 49
Joined: Sun Mar 15, 2015 3:11 pm

Re: BS - Vignette Attempt - Please Review!

Postby Coach » Wed Oct 18, 2017 2:00 pm

bradfordpayne wrote:I calculated the 2x4 lights to be 4' spacing on the 2' end and 6' spacing on the 4' end.

Correct, but that's not what you did in AO.

I still have the accent lights at 4' spacing, but overlapped the sketch circles to give more of a 1'-8" spacing. Is this correct?

Circles must intersect at wall. Depending on layout, accents will end up 12", 16", or 20" from wall.

Is there adequate air movement in the studio now?

Yes.

Maintain 4' min between S & R grilles.
I would move south reception grilles 2' west.
Move eastern duct to just west of conf wall.
Long side of return grilles must be on grid or fixture.
Place long damper leg in wall.
Using circles for anything but accents is a waste of time.

User avatar
Coach
Site Admin
 
Posts: 13249
Joined: Wed May 23, 2012 2:08 am


Return to BS - BUILDING SYSTEMS

Who is online

Users browsing this forum: No registered users and 66 guests

cron