Vignette Feedback

Mechanical & Electrical Plan Vignette and Multiple Choice

Vignette Feedback

Postby danieb1 » Sat Jul 15, 2017 6:55 pm

Anyone care to comment?

Thanks
You do not have the required permissions to view the files attached to this post.
danieb1
 
Posts: 41
Joined: Mon Jul 25, 2016 7:43 pm

Re: Vignette Feedback

Postby Sparky83 » Sun Jul 16, 2017 5:22 am

Missing flex in the architect's office. Rigid cannot connect to diffusers.
Uneven HVAC layout in the studio. Think symmetry.
Poor separation between supply & return in the conference room. Min 4' is recommended.
Lights are not centered in the file room.
Not much air movement in the center of reception.
Too many accent lights and too far from the wall. The sketch circles should intersect each other at the face of the wall.
Dampers should be in the center of the wall thickness.
Sparky83
 
Posts: 7649
Joined: Tue Dec 02, 2014 1:36 pm

Re: Vignette Feedback

Postby danieb1 » Sun Jul 16, 2017 8:09 am

Thanks, Sparky.

You brought up a question that's been puzzling me about the accent lights. If they are moved closer to the wall the Fc directly in front of the light would be way over 80. Is this not problematic for the exam?
danieb1
 
Posts: 41
Joined: Mon Jul 25, 2016 7:43 pm

Re: Vignette Feedback

Postby Sparky83 » Sun Jul 16, 2017 4:49 pm

danieb1 wrote:Thanks, Sparky.

You brought up a question that's been puzzling me about the accent lights. If they are moved closer to the wall the Fc directly in front of the light would be way over 80. Is this not problematic for the exam?