introversed wrote:Comments Appreciated!
=The return duct pokes out beyond the bearing wall slightly. I felt uneasy ending it at the damper. Please confirm. Damper should be centered in the wall thickness.
Also, because the supply diffuser in the supply closet is aligned with the rigid duct, I have that diffuser's flexible duct going one snap vertically to ensure its connection to the rigid duct. Please confirm this is ok. Thanks Not ok. Move the rigid duct or move the diffuser.
Architect's office is under lit. Lights are not centered.
Need to see sketch elements to evaluate accent lights.
Lights are not centered in the studio or conference room.
Supply closet is severely under lit.
Rigid layout does not allow for flexibility in diffuser location given a 10' max flex.
HVAC layout in the studio is not uniform. Think symmetry.