by Sparky83 » Tue May 16, 2017 5:40 pm
Sorry, that's a mess.
Return riser connected to diffusers, and supply riser connected to plenum. FATAL.
Incorrect 2x4 light spacing in every room. Every room is incorrectly lit. You must use BOTH lighting charts for 2x4 lights. It is VERY unlikely that you can use one lighting type for the entire solution.
Light perpendicular to and overlapping grid in reception.
Lights not centered in the architect's office.
Cannot see flex in the conference room.
Uneven HVAC layout in the studio.
Cannot evaluate accent lights without sketch elements showing.
Poor separation between supply & return in the supply closet. Min 4' is recommended.