Vignette 1st try-please comment!

Mechanical & Electrical Plan Vignette and Multiple Choice

Vignette 1st try-please comment!

Postby aejewett » Tue May 16, 2017 5:24 pm

This was my first attempt :)
You do not have the required permissions to view the files attached to this post.
aejewett
 
Posts: 16
Joined: Mon Jan 02, 2017 10:45 am

Re: Vignette 1st try-please comment!

Postby Sparky83 » Tue May 16, 2017 5:40 pm

Sorry, that's a mess.
Return riser connected to diffusers, and supply riser connected to plenum. FATAL.
Incorrect 2x4 light spacing in every room. Every room is incorrectly lit. You must use BOTH lighting charts for 2x4 lights. It is VERY unlikely that you can use one lighting type for the entire solution.
Light perpendicular to and overlapping grid in reception.
Lights not centered in the architect's office.
Cannot see flex in the conference room.
Uneven HVAC layout in the studio.
Cannot evaluate accent lights without sketch elements showing.
Poor separation between supply & return in the supply closet. Min 4' is recommended.