PostPosted: Mon Nov 09, 2015 10:28 am
by arewethereyet_882
Hi Guys, I have exam tomorrow yet I'm still puzzled about which electrical conduit cannot be embedded in concrete or underground ? I received mixed answers from Kaplan, Ballast, and Amber Book, so would like to verify with everyone. Choices are as follows

Rigid Conduit (RMC)

Electrical Mettalic Tubing (EMT)

Intermediate Metal Conduit (IMC)

Flexible Metallic Conduit

Armor Conduit

Romex/ Nonmetallic Sheathed Cable


Which one is it that cannot be embedded in concrete or used in underground?

Thanks very much.

Re: Electrical Metal Conduit

PostPosted: Mon Nov 09, 2015 12:45 pm
by cathaejo
Flexible metal conduit

Re: Electrical Metal Conduit

PostPosted: Mon Nov 09, 2015 1:18 pm
by arewethereyet_882
Thanks Cathaejo. This is what I originally thought, however when I encountered this question in Kaplan Q&A practice question (#62), and the answer turned out to be "Armored cables", as oppose to flex metal conduit .... This is why I'm confused....

Re: Electrical Metal Conduit

PostPosted: Mon Jun 25, 2018 5:51 pm
by matt
Blast same question that I have and testing tomorrow

Re: Electrical Metal Conduit

PostPosted: Tue Jun 26, 2018 6:25 am
by JSLove
Flexible metal conduit definitely cannot be used in those locations. Armored cable cannot be used for direct burial in earth, but can be embedded in concrete only with a lead-covered conductor (ACL). I got that Kaplan question wrong too and it didn't make sense to me why I did, so I did a little research. :P