Postby jijiniuniu » Tue Jun 19, 2018 12:54 pm

Please kindly review and advise.

Thanks
You do not have the required permissions to view the files attached to this post.
jijiniuniu
 
Posts: 69
Joined: Thu Dec 19, 2013 7:55 pm

Re: BS - Vignette 01 - Please review

Postby Sparky83 » Tue Jun 19, 2018 1:31 pm

The rigid duct layout does not allow for flexibility in placement of diffusers. With a max 10' flex, there are large areas that cannot be reached.
Need to see sketch elements to evaluate accent lights.
Sparky83
 
Posts: 7649
Joined: Tue Dec 02, 2014 1:36 pm

Re: BS - Vignette 01 - Please review

Postby jijiniuniu » Tue Jun 19, 2018 5:44 pm

@ Sparky83

Thank you. how about this one ? can the rigid duct cross the light fixtures?

Thanks
You do not have the required permissions to view the files attached to this post.
jijiniuniu
 
Posts: 69
Joined: Thu Dec 19, 2013 7:55 pm

Re: BS - Vignette 01 - Please review

Postby jijiniuniu » Tue Jun 19, 2018 9:09 pm

One more try. sounds like this kind of solution more safe, since it is more similar to the passing solution of NCARB.

Does duct work efficiency matter ? I was told the diffuses at the same room should connect to the same secondary rigid duct ? is that true ?

thoughts ? advice ?

Thanks
You do not have the required permissions to view the files attached to this post.
jijiniuniu
 
Posts: 69
Joined: Thu Dec 19, 2013 7:55 pm

Re: BS - Vignette 01 - Please review

Postby Coach » Tue Jun 19, 2018 11:08 pm

jijiniuniu wrote:Does duct work efficiency matter ?

Reasonable efficiency matters but you must provide flexibility with good coverage. In this solution for example, you can delete ducts south of shaft, move other branches west, and still have good suite coverage.

I was told the diffuses at the same room should connect to the same secondary rigid duct ? is that true ?

No.
User avatar
Coach
Site Admin
 
Posts: 13249
Joined: Wed May 23, 2012 2:08 am

Re: BS - Vignette 01 - Please review

Postby jijiniuniu » Wed Jun 20, 2018 12:58 am

Thank you Coach.

1. rigid duct : do you mean this layout ? tow vertical main branches instead of 1 or 3 ?
2. flex duct: to make the above happen, I have to connect the 3 diffusers at the the drafting studio to 2 different rigid branches. it conflicts with the Jenny's notes. But as you mentioned, it might not be a big deal
3. location of diffuses : some people mentioned to put all of the diffusers at one row and all of the returns at the other side. Is it a good strategy ? or we would better distribute the diffuser at diagonal potions?

Please advise. Thanks
You do not have the required permissions to view the files attached to this post.
jijiniuniu
 
Posts: 69
Joined: Thu Dec 19, 2013 7:55 pm

Re: BS - Vignette 01 - Please review

Postby Sparky83 » Wed Jun 20, 2018 3:47 am

jijiniuniu wrote:One more try. sounds like this kind of solution more safe, since it is more similar to the passing solution of NCARB. Your 2nd solution is more efficient.

Does duct work efficiency matter ? I was told the diffuses at the same room should connect to the same secondary rigid duct ? is that true ? Nope. It all comes from the same riser.

thoughts ? advice ?

Thanks

Those tips contain several errors.
Light distance from the wall depends on the lighting charts.
Diffusers can be anywhere in the room. Symmetry and distance from return grilles matters. Doors and windows do not matter at all.
Duct lines are NOT centerlines. This is entirely schematic.
Supply & return can be all on one side.

People like to make stuff up.
Sparky83
 
Posts: 7649
Joined: Tue Dec 02, 2014 1:36 pm

Re: BS - Vignette 01 - Please review

Postby jijiniuniu » Wed Jun 20, 2018 10:35 am

Quite appreciate it . Sparky83 !

one more question : can the distance between the two rigid ducts be more than 20' ?

Thanks
You do not have the required permissions to view the files attached to this post.
jijiniuniu
 
Posts: 69
Joined: Thu Dec 19, 2013 7:55 pm

Re: BS - Vignette 01 - Please review

Postby Sparky83 » Fri Jun 22, 2018 4:26 am

...
Last edited by Sparky83 on Fri Jun 22, 2018 4:27 am, edited 1 time in total.
Sparky83
 
Posts: 7649
Joined: Tue Dec 02, 2014 1:36 pm

Re: BS - Vignette 01 - Please review

Postby Sparky83 » Fri Jun 22, 2018 4:26 am

jijiniuniu wrote:Quite appreciate it . Sparky83 !

one more question : can the distance between the two rigid ducts be more than 20' ?

Thanks

Not recommended.
Sparky83
 
Posts: 7649
Joined: Tue Dec 02, 2014 1:36 pm

Re: BS - Vignette 01 - Please review

Postby jijiniuniu » Fri Jun 22, 2018 7:12 am

Many thanks sparky
jijiniuniu
 
Posts: 69
Joined: Thu Dec 19, 2013 7:55 pm