went for speed this time. noticed my return damper's facing wrong direction. also probably should have spaced diffusers/grilles further apart in conference..had a last minute issue in this area and didn't second check :( are these considered big errors?

anything else?
You do not have the required permissions to view the files attached to this post.
mpc123
 
Posts: 74
Joined: Sat Aug 15, 2015 11:39 pm

Re: testing tomorrow - comments please!

Postby Sparky83 » Thu Oct 19, 2017 4:31 am

The rigid duct layout does not provide flexibility in relocating diffusers per the program. With a max 10' flex, there are large areas that cannot be reached.
No air movement on the west side of the architect's office.
Poor separation between supply & return in the conference room and studio. MIn 4' separation is recommended.
Uneven HVAC layout in the studio and conference room. Think symmetry.
Accent lights are a little too close to the wall. Sketch circles should intersect each other at the face of the wall being lit.
Sparky83
 
Posts: 7649
Joined: Tue Dec 02, 2014 1:36 pm

Re: testing tomorrow - comments please!

Postby mpc123 » Thu Oct 19, 2017 8:07 am

Thank you. So would it have been better to have 2 rows of rigid duct for more balanced air distribution? I’ve been under impression less rigid duct is better. But let me know your thoughts.
mpc123
 
Posts: 74
Joined: Sat Aug 15, 2015 11:39 pm

Re: testing tomorrow - comments please!

Postby Coach » Thu Oct 19, 2017 9:08 am

Basic efficiency is good but an explicit part of the program is flexibility.