Vignette- Review/feedback is greatly appreciated

Mechanical & Electrical Plan Vignette and Multiple Choice

Vignette- Review/feedback is greatly appreciated

Postby jeremyj » Wed Jul 26, 2017 7:45 pm

Hello Forum,

Any feedback on vignette is appreciated. My main concern is about adequate lighting coverage and of course any other issues that require feedback.

Thank you and much appreciated.
You do not have the required permissions to view the files attached to this post.
jeremyj
 
Posts: 19
Joined: Sat Feb 27, 2016 11:12 am

Re: Vignette- Review/feedback is greatly appreciated

Postby dsekerak » Thu Jul 27, 2017 6:29 pm

1. Rigid duct has to be with 2' zone of bearing walls and can't pass through joists. I believe thats a biggie.
2. accent lighting needs to have a 2'radius sketch circle to layout fixtures and the circles need to overlap each other at the face of the wall to distribute lighting equally. way too much lighting at 5' w/ this layout.
3. make sure diffusers and returns are min. 4' away from each other.
4. flex duct can't be longer than 10'. couple in the drafting studio look to be close to that.
5. I think you may be overlighting the supply closet.
6. distribution of diffusers in conference room can be a little better.

I think the biggest thing here is the rigid ductwork placement. be sure you are running parallel with joists unless you are within 2' of bearing walls.

Best of luck saturday. I am testing that day as well. Hopefully to be completely done with this ARE process. Hope this helps.

dan
dsekerak
 