Sparky83 wrote:Why is there a return grille outside the east exterior wall? Major error.
Rotate 2x4 lights in the architect's office for more uniform coverage.
Accent lights are too far apart. Sketch circles should intersect each other at the face of the wall being lit.
Grilles not supported on 3 sides will fall out. See studio, reception, file room and architect's office.
Lights in the conference room are not centered.
aninaz wrote:Sparky83 wrote:Why is there a return grille outside the east exterior wall? Major error.
Rotate 2x4 lights in the architect's office for more uniform coverage.
Accent lights are too far apart. Sketch circles should intersect each other at the face of the wall being lit.
Grilles not supported on 3 sides will fall out. See studio, reception, file room and architect's office.
Lights in the conference room are not centered.
Thank you so mich for comments. I didn't quite undrestand what does that mean grilles not supported on 3 sides will fall out. Would you olease explain more? Thank you