Postby angelw » Sun Oct 04, 2015 1:07 pm

I don't think I'm grasping this vignette really...any suggestions would be great, thanks!
You do not have the required permissions to view the files attached to this post.
angelw
 
Posts: 37
Joined: Tue Feb 03, 2015 2:52 pm

Re: Vignette - First try

Postby ren4ARE » Sun Oct 04, 2015 2:37 pm

Vignette_10.04.15.jpg


angelw, I think this might help... http://are-resources.weebly.com/bs-vignette.html

1) Grilles should be supported on at least 3 sides
2) Use sketch circles to figure out the accent light levels. Review the forum for tips on accent levels
3) Somewhere I read that the short leg should point in the direction of air flow. Not sure if it really matters because the Ncarb passing solution shows what you have drawn
4) Align your diffusers with the ceiling grid
5) I have read that you need a 4' min separation between grille and diffuser.

Check out my comments on your solution as well as the link. You'll get this vignette in no time!

Good luck!
-REN
You do not have the required permissions to view the files attached to this post.
ren4ARE
 
Posts: 43
Joined: Thu Mar 26, 2015 8:31 pm

Re: Vignette - First try

Postby Sparky83 » Sun Oct 04, 2015 5:08 pm

Uneven lighting in the studio. NEVER mix 2x2 and 2x4 lights in a room.
NW grille in the architect's office will fall out.
Insufficient accent lighting.
There is ZERO evidence that the direction of the damper symbol matters at all. All we know is that the long leg must be parallel to the wall.
You have a flex from the return rigid duct leading to a diffuser in reception. Not a good idea. That means you have no plenum return. Fatal.
Ducts may be placed above lights.
Sparky83
 
Posts: 7649
Joined: Tue Dec 02, 2014 1:36 pm

Re: Vignette - First try

Postby angelw » Sun Oct 04, 2015 6:35 pm

Thanks for the help! will work on this one a bit more and post again.
angelw
 
Posts: 37
Joined: Tue Feb 03, 2015 2:52 pm