BL 3rd Pass

Interior Layout & Building Layout Vignettes

BL 3rd Pass

Postby catonahighhorse » Fri Oct 13, 2017 7:28 pm

Hi All and thanks for your comments. These images show (1) layer at a time so that the windows could be better seen. I eyeballed their placement, but kept lengths consistent at either 4 or 5 feet in length depending on the room. Hope that is okay.
You do not have the required permissions to view the files attached to this post.
catonahighhorse
 
Posts: 27
Joined: Thu Jan 19, 2017 12:53 pm

Re: BL 3rd Pass

Postby Coach » Wed Oct 18, 2017 1:39 pm

catonahighhorse wrote:These images show (1) layer at a time so that the windows could be better seen. I eyeballed their placement, but kept lengths consistent at either 4 or 5 feet in length depending on the room. Hope that is okay.

No need for consistent lengths. Eyeball those too.


Illegal dead end @ 1st floor east. Dead end measured to center of stair door.
MP doors to circulation must swing out.
CR & TS/MP distances unnecessarily weak. Move MP door to west end and CR door east.
User avatar
Coach
Site Admin
 
Posts: 13249
Joined: Wed May 23, 2012 2:08 am

Re: BL 3rd Pass

Postby catonahighhorse » Fri Oct 20, 2017 7:55 am

Thanks
catonahighhorse
 
Posts: 27
Joined: Thu Jan 19, 2017 12:53 pm