BL Second Try

Interior Layout & Building Layout Vignettes

BL Second Try

Postby catonahighhorse » Tue Oct 10, 2017 8:38 am

Hello, here is the 2nd try at the BL layout for your comments and critique. Thanks.
You do not have the required permissions to view the files attached to this post.
catonahighhorse
 
Posts: 27
Joined: Thu Jan 19, 2017 12:53 pm

Re: BL Second Try

Postby catonahighhorse » Tue Oct 10, 2017 10:01 am

Just realised the EE is missing its door. Assume access from MP space.Thanks
catonahighhorse
 
Posts: 27
Joined: Thu Jan 19, 2017 12:53 pm

Re: BL Second Try

Postby Sparky83 » Tue Oct 10, 2017 11:12 am

Illegal dead-end to SW. Fatal.
TR's do not have to stack.
MP must have 2 exits. You have only 1. Exit doors MUST swing in the direction of egress.
Cannot see windows...interior or exterior.
Sparky83
 
Posts: 7649
Joined: Tue Dec 02, 2014 1:36 pm

Re: BL Second Try

Postby catonahighhorse » Thu Oct 12, 2017 11:05 am

Thank you for your comments. Per Prof. Dorf's comments and the feedback from this post, would it be reasonable to define a dead end as a corridor that does not have exit stairs at its end?
catonahighhorse
 
Posts: 27
Joined: Thu Jan 19, 2017 12:53 pm

Re: BL Second Try

Postby Sparky83 » Thu Oct 12, 2017 2:08 pm

catonahighhorse wrote:Thank you for your comments. Per Prof. Dorf's comments and the feedback from this post, would it be reasonable to define a dead end as a corridor that does not have exit stairs at its end?

No. Corridors have 2 ends. A corridor may end at a lobby or an exit to the exterior at one or both ends. A corridor may end at another corridor that leads to an exit.
Sparky83
 
Posts: 7649
Joined: Tue Dec 02, 2014 1:36 pm

Re: BL Second Try

Postby catonahighhorse » Fri Oct 13, 2017 7:18 pm

Correct, I should have been more careful with my words, I meant a corridor that meets one of the conditions listed in your reply on one end, but does not have an exit at the other end. This condition of one directional exit travel must be kept under 20 feet as I understand it.
catonahighhorse
 
Posts: 27
Joined: Thu Jan 19, 2017 12:53 pm

Re: BL Second Try

Postby Coach » Wed Oct 18, 2017 1:32 pm

catonahighhorse wrote:Correct, I should have been more careful with my words, I meant a corridor that meets one of the conditions listed in your reply on one end, but does not have an exit at the other end. This condition of one directional exit travel must be kept under 20 feet as I understand it.

A dead end is any point in a corridor from which you have only one direction of egress.
User avatar
Coach
Site Admin
 
Posts: 13249
Joined: Wed May 23, 2012 2:08 am


Return to SD - SCHEMATIC DESIGN