BL - Please review and comment

Interior Layout & Building Layout Vignettes

BL - Please review and comment

Postby kkao » Mon Oct 02, 2017 7:39 pm

171002_BL (2).PNG
171002_BL.PNG
Thank you!
You do not have the required permissions to view the files attached to this post.
kkao
 
Posts: 10
Joined: Mon Feb 01, 2016 6:46 pm

Re: BL - Please review and comment

Postby Sparky83 » Tue Oct 03, 2017 4:22 am

GR does not have the required view.
Why is there a window in the north wall of GR?
Why is there a direct connection between R and CR?
Stairs have no exits. MAJOR life safety error. Fatal.
MP must have 2 exits. You show only 1. Exit doors MUST swing in the direction of egress.
LR's are twice the required size.
EM must have a direct connection to circulation.
E should NOT have a door.
Missing wall opening upstairs. SO, DO, and both TR's are inaccessible.
Avoid L-shaped rooms.