Postby krissmZ » Sat Mar 03, 2018 12:26 pm

Can you please review the attached roof NCARB solution? Is it ok that the gutter goes in front of the chimney? Or should it break? If I break then it will require 2 more downspouts on either side of the chimney, so which is considered more efficient and a better design?

Do I always need a downspout on either end of a gutter?

Is it a good solution to have the top and bottom roofs meet at the same elevation in order to use one gutter? I realize I you can't tell the roof elevations, but they are both 9'-6" on the East side.

NCARB - ROOF - ZARELLA - 2018_0302.jpg
You do not have the required permissions to view the files attached to this post.
krissmZ
 
Posts: 66
Joined: Sun Apr 26, 2015 5:01 pm

Re: Roof Vignette - Please Review!

Postby Coach » Sat Mar 03, 2018 7:37 pm

krissmZ wrote:Is it ok that the gutter goes in front of the chimney?

No reason not to.

Do I always need a downspout on either end of a gutter?

One is enough up to 15'.

Is it a good solution to have the top and bottom roofs meet at the same elevation in order to use one gutter?

No. Upper must be above lower wherever they meet. Roof planes should have their own gutters and gutters should not share downspouts.

I realize I you can't tell the roof elevations, but they are both 9'-6" on the East side.

See above.