Ramp, Stair, & Roof Vignettes and Multiple Choice
by kkao » Mon Jan 29, 2018 8:34 pm
Thank you!
You do not have the required permissions to view the files attached to this post.
-
kkao
-
- Posts: 10
- Joined: Mon Feb 01, 2016 6:46 pm
by architerp » Tue Jan 30, 2018 7:15 am
Roof:
Looks like you put gutters at gables. Not necessary.
Make sure downspouts are associated to the proper roof. The west ds near the door looks to be too far south.
Avoid hip roofs.
Your high point of the high roof is 27'-1". Your roof ridges likely do not meet. Check spot dimensions for all corners of all roofs. Use the "Check" tool for the roof boundaries too.
Ramp:
I don't believe it's possible to get from 30" to 25" at the first landing. Check your run distance.
Stair may be too narrow?
The 3" landing could be a left turn out instead of a U-turn.
Stair:
Looks good to me.
-
architerp
-
- Posts: 51
- Joined: Thu Dec 12, 2013 12:43 pm
by Sparky83 » Tue Jan 30, 2018 7:48 am
architerp wrote:Roof:
Looks like you put gutters at gables. Not necessary.
Make sure downspouts are associated to the proper roof. The west ds near the door looks to be too far south.
Avoid hip roofs. The hip roof on the lower level works just fine.
Your high point of the high roof is 27'-1". Your roof ridges likely do not meet. Check spot dimensions for all corners of all roofs. Use the "Check" tool for the roof boundaries too.
Ramp:
I don't believe it's possible to get from 30" to 25" at the first landing. Check your run distance.
Stair may be too narrow?
The 3" landing could be a left turn out instead of a U-turn.
Stair:
Looks good to me.
-
Sparky83
-
- Posts: 7649
- Joined: Tue Dec 02, 2014 1:36 pm
Return to BDCS - BUILDING DESIGN & CONSTRUCTION SYSTEMS
Who is online
Users browsing this forum: No registered users and 42 guests