Roof 3.1_please comment

Ramp, Stair, & Roof Vignettes and Multiple Choice

Roof 3.1_please comment

Postby pig » Tue Dec 05, 2017 9:00 pm

testing tomorrow...
kindly pls see if i have made any mistakes?
You do not have the required permissions to view the files attached to this post.
pig
 
Posts: 111
Joined: Thu Feb 26, 2015 2:38 pm

Re: Roof 3.1_please comment

Postby Archer40 » Tue Dec 05, 2017 9:28 pm

A couple things:
-missing flashing around chimney
-missing 1 exhaust fan vent for the break room (required by program)
-elevation of upper volume roof needs to be higher (the 15’-8” elevation needs to be at least 17’-2” to accommodate the 30” high clerestory and 18” thick roof structure)
Archer40
 
Posts: 145
Joined: Thu Jul 14, 2016 8:51 pm

Re: Roof 3.1_please comment

Postby pig » Tue Dec 05, 2017 9:30 pm

oooooh!! thank you so much Archer40!!
would this be correct now....? i also notice i missed a skylight at the female restroom too!
You do not have the required permissions to view the files attached to this post.
pig
 
Posts: 111
Joined: Thu Feb 26, 2015 2:38 pm

Re: Roof 3.1_please comment

Postby Coach » Tue Dec 05, 2017 11:05 pm

pig wrote: i also notice i missed a skylight at the female restroom too!

No, it has a window.

Missing downspouts.
Missing pvent.
Missing exhaust.