CDS Section - Testing in a few days!

PostPosted: Sat Aug 05, 2017 5:59 pm
by dilwilli
Hello,
I test in a few days. Please take a look and let me know if I've missed anything.
Thank you!
Dillon

Re: CDS Section - Testing in a few days!

PostPosted: Tue Aug 08, 2017 7:31 pm
by dilwilli
Here is the section without the background for clarity.
I test Thursday morning so any comments would be greatly appreciated!

Re: CDS Section - Testing in a few days!

PostPosted: Wed Aug 09, 2017 5:25 am
by thd7t
Your non-rated wall should only go 6" above ceiling.

Re: CDS Section - Testing in a few days!

PostPosted: Wed Aug 09, 2017 6:13 pm
by dilwilli
Good catch. Thank you!

Re: CDS Section - Testing in a few days!

PostPosted: Wed Aug 30, 2017 12:54 pm
by Sfny
it looks like the space you allowed for the ducts and lighting for the Lab is not deep enough

confirm that you have added the correct numbers for clearances -
the joist duct and light space for the Lab is 20"+8"= 28" (2'-4")
the joist and deck assembly for the Lab is 32" + 4"- 36" (3'-0") total 5'-4" above 15'